since the risks of scolding is there, (you run the engine for a day to reach your destination) then you need some thermostatic control of the water coming out of the calorifier. Even with uninsulated small bore pipes (mine are 15mm inside diameter) the heatloss from the pipes and calorifier has to be greater than the Watts of energy going in to the calorifier or the temperature of the stored water in the calorifier will elevate. Rubber hose is a surprisingly good insulator. The heat loss from plain unfinned pipes is only a few watts per meter. Believe me, if I run our hot tap to the galley for a minute the water temperature is scolding. We have it like this on purpose as it means a relatively small calorifier can store a lot of energy. You have to be very aware of the risks. The risk isn't worth taking with a shower so top quality thermostatic valves are essential
Just got some tables out. Assume 55degC difference between water in pipe and engine room. 15mm copper pipe. Heat loss is 45w/m run of pipe. Copper will be far better at losing heat than rubber