Lon nan Gruagach
Well-Known Member
Its already C rated 32 amps !
And it runs everything except air con just fine. Plug in a switched off air con and it goes poof.
Its already C rated 32 amps !
Its already C rated 32 amps !Sounds like a in rush current problem as others have said up rate the trip rating.![]()
Its already C rated 32 amps !
Guys he has two shore power leads
To two seperate sockets on the boat .
One is dedicated for the Aircon .
With the Aircon OFF as soon as the shore power lead ( which works ok on the other domestic and his neighbors ) is pugged in / touches this socket the shore rcd trips .
He has not even turned the Aircon on yet .
How ever he knows the Aircon bits work ok via the geny .
So the fault s gotta be in that socket - most likely wet or some other reason for it shorting .
The lead s all work in the other domestic and the neighbors- so it’s not a damp lead / plug
It’s not tripping switching the Aircon on - it’s allready tripped on shore by the time he,s walked from the transom to the saloon as soon as any plug is inserted into this dedicated Aircon socket !
The other domestic side is fine so he can get alternating current to his “ sockets “ say to boil a kettle etc .
——— similar fault which initially only manifested its self when connected to shorepower then caused tripping when run through the generator as well.
![]()