!2v Guru needed

Cousin Jack

Member
Joined
23 Feb 2010
Messages
34
Location
Falmouth
Visit site
What I thought would be a simple exchange exercise is proving a little more demanding....removed one old 12v cabin light, put a new one on, nothing! Having changed bulbs etc, I eventually put a meter on the supply, 12.56v present, lights before and after working, put a load, (std bulb, that works!), in the circuit, and the meter reads 0.00v!

Any thoughts??
 
What I thought would be a simple exchange exercise is proving a little more demanding....removed one old 12v cabin light, put a new one on, nothing! Having changed bulbs etc, I eventually put a meter on the supply, 12.56v present, lights before and after working, put a load, (std bulb, that works!), in the circuit, and the meter reads 0.00v!

Any thoughts??

You've got a bad connection somewhere, which is working until it has to pass significant current. Probably a corroded bullet connector, or a dirty or corroded bulb socket.
 
This one is easy but it might be a bugger to find. There is a corroded connection somewhere that is preventing the circuit from carrying load. I'd use a test bulb at various points to chase it back until you find the issue. A bulb will provide enough load to recreate the fault.
Try checking at the switch/breaker first.... at least you'll have a good starting point then...
 
Thanks Chaps, that should keep me out of trouble for a while!!

This one is easy but it might be a bugger to find. There is a corroded connection somewhere that is preventing the circuit from carrying load. I'd use a test bulb at various points to chase it back until you find the issue. A bulb will provide enough load to recreate the fault.
Try checking at the switch/breaker first.... at least you'll have a good starting point then...
 
Thanks Chaps, that should keep me out of trouble for a while!!
Without doubt a bad connection


One of the pitfalls of using a digital volt meter. They take so little current that they give a normal reading despite there being a bad connection.

A test lamp. ( a small bulb on a couple of leads ) is what you need ........ or even the meter with a small bulb in parallel
 
Without doubt a bad connection


One of the pitfalls of using a digital volt meter. They take so little current that they give a normal reading despite there being a bad connection.

A test lamp. ( a small bulb on a couple of leads ) is what you need ........ or even the meter with a small bulb in parallel

That's what I did when tested under load, (bulb and meter)....old habits etc.

Thanks
 
One thing that exhibits exactly this behaviour is those fuses which have an LED which light up when blown....
 
One of the pitfalls of using a digital volt meter. They take so little current that they give a normal reading despite there being a bad connection.

+1 - I ended up buying an unnecessary replacement fridge controller as a result of this mistake :(

Pete
 