John100156
Well-Known Member
There are a couple of other factors that you may need to consider when selecting a cable size: grouping of circuits, thermal insulation and if the cables run through a hot area.
All of the above can reduce the current carrying capacity of a cable. You also need to consider the length of run of course.
If you install a 16A RCD or Fuse, the type of device fitted (time/current characteristics) will also influence the maximum recommended current carrying capacity of the circuit cabling.
So, I would probably go for 2.5mm2 tinned stranded cable, as has been said, to avoid corrosion issues, it is also better particularly where the loom could move.
Making the circuit a ring increases the current carrying capacity of the primary conductors in that circuit.
On most boats you could probably use a 1.5mm2 ring with no problems at all, the circuit length is usually short; but if I were installing this circuit on my boat, I would certainly go for 2.5mm2. The cost diffecerence is not too significant and the volt drop across the cable will be less.
When taking a cable from the main RCD on a boat, it must of course be rated to carry the maximum current of all installed loads, this size of cable must run to the input side of all breakers/fuses before they drop down to serve circuits with a lesser rated breaker/fuse and cable size.
All clear as mud!
All of the above can reduce the current carrying capacity of a cable. You also need to consider the length of run of course.
If you install a 16A RCD or Fuse, the type of device fitted (time/current characteristics) will also influence the maximum recommended current carrying capacity of the circuit cabling.
So, I would probably go for 2.5mm2 tinned stranded cable, as has been said, to avoid corrosion issues, it is also better particularly where the loom could move.
Making the circuit a ring increases the current carrying capacity of the primary conductors in that circuit.
On most boats you could probably use a 1.5mm2 ring with no problems at all, the circuit length is usually short; but if I were installing this circuit on my boat, I would certainly go for 2.5mm2. The cost diffecerence is not too significant and the volt drop across the cable will be less.
When taking a cable from the main RCD on a boat, it must of course be rated to carry the maximum current of all installed loads, this size of cable must run to the input side of all breakers/fuses before they drop down to serve circuits with a lesser rated breaker/fuse and cable size.
All clear as mud!