Well-Known Member
I have a simple mains distribution panel in my boat. The breaker switches have decided not to remain in the “on” position even when nothing is connected to them. Which I don’t understand. It has been working fine.
Also, I get 240v when I measure from the earth bussbar to the neutral bussbar, which seems most odd. Surely there should be no voltage on the earth at all?
If there is a fault somewhere with a mains appliance it could be sending volts down the earth. I have a galvanic isolator which is not showing a fault. But with nothing connected where are these volts coming from on the earth?
Also, I get 240v when I measure from the earth bussbar to the neutral bussbar, which seems most odd. Surely there should be no voltage on the earth at all?
If there is a fault somewhere with a mains appliance it could be sending volts down the earth. I have a galvanic isolator which is not showing a fault. But with nothing connected where are these volts coming from on the earth?