LFP voltage drop under load

roaringgirl

Well-known member
Joined
1 Nov 2014
Messages
886
Location
Half way around: Wellington, NZ.
bit.ly
Hi, I have a 400Ah, 12V LFP battery. At 75% charge state (according to the shunt) the voltage is 13.3. When drawing a little over 100A, the voltage dips to 12.5 and recovers immediately that the load is removed. Is this normal/reasonable? What is the relationship between voltage drop and load? Is it linear?

Thanks
 

William_H

Well-known member
Joined
28 Jul 2003
Messages
13,626
Location
West Australia
Visit site
I don't know if this is reasonable for that battery. 100Amps will test connections and wiring. So is this a measurement of battery voltage at the terminals? If so then you might like to check actual voltage of individual cells under load. If one tends to drop more than the others then you may have a faulty cell. If they all seem to drop similar amounts then yes that is the best your battery can do.
If you are reporting what your control panel tells you then it may be wiring drop. Connect a multimeter between positive terminal of battery and any positive point at panel. this may indicate a volt drop in wiring including any isolation switch etc. Do same with negative line battery to panel. ol'will
 

geem

Well-known member
Joined
27 Apr 2006
Messages
7,236
Location
Caribbean
Visit site
Hi, I have a 400Ah, 12V LFP battery. At 75% charge state (according to the shunt) the voltage is 13.3. When drawing a little over 100A, the voltage dips to 12.5 and recovers immediately that the load is removed. Is this normal/reasonable? What is the relationship between voltage drop and load? Is it linear?

Thanks
That does seem a little low. Our 280Ah 24v bank with 100 amp load drops to +26v when at circa 80%. What kind of lithium? Drop in or custom build? What kind of bms? Active balance or passive?
 

Poey50

Well-known member
Joined
26 Apr 2016
Messages
2,309
Location
Chichester
Visit site
Hi, I have a 400Ah, 12V LFP battery. At 75% charge state (according to the shunt) the voltage is 13.3. When drawing a little over 100A, the voltage dips to 12.5 and recovers immediately that the load is removed. Is this normal/reasonable? What is the relationship between voltage drop and load? Is it linear?

Thanks
My hunch is that your state of charge is off and is much lower in reality. Because of the flat discharge curve 13.3 volts may apply to a wide range of states of charge.
 
  • Like
Reactions: vas

roaringgirl

Well-known member
Joined
1 Nov 2014
Messages
886
Location
Half way around: Wellington, NZ.
bit.ly
That does seem a little low. Our 280Ah 24v bank with 100 amp load drops to +26v when at circa 80%. What kind of lithium? Drop in or custom build? What kind of bms? Active balance or passive?
It's 2 Victron 200Ah batteries. They each have their own internal BMS and one external sitting over them both. The cells get balanced by the BMS on a full charge.
 

geem

Well-known member
Joined
27 Apr 2006
Messages
7,236
Location
Caribbean
Visit site
I'd be interested to know what you are using onboard that draws 100 amps. I struggle to get up to 10 amps.
For us it's the immersion heater (50A), watermaker (77A), kettle (105A), induction hob (83A) all at 24v so double it for 12v system. 280Ah lithium battery at 24v
 

roaringgirl

Well-known member
Joined
1 Nov 2014
Messages
886
Location
Half way around: Wellington, NZ.
bit.ly
How does that work? Two BMS's?

According to Victron:
Victron LiFePO4 batteries have integrated Balancing, Temperature and Voltage control (acronym: BTV) and connect to the VE.Bus BMS with two M8 circular connector cord sets.
The BTVs of several batteries can be daisy chained. Please see our LiFePO4 battery documentation for details.

The BMS will:

Shut down or disconnect loads in case of imminent cell under voltage
Reduce charge current in case of imminent cell overvoltage or over temperature (VE.Bus products only, see below)
Shut down or disconnect battery chargers in case of imminent cell overvoltage or over temperature
 