Sorry for this post if the answer is obvious but its not to me.....
I would like to protect against a fire from the battery main cables. But I don't want to create a situation where the fuse occasionally blows for other reasons as this could for example then blow my alternator diodes, so I want to be absolutely certain that the fuse will not blow under any general usage circumstances but would protect against the situation where the wire became so hot that there was a danger of it catching on fire.
I think the biggest slow blow fuse is 750a and I would have imagined that this would always blow before a large cale (50-90mm) caused a fire ???
There has been some other pbo posts where the recommended fuse for the wire size has been suggested. Here they are...
cable size fuse
35mm2 264A
AWG 1 305A
50mm2 345A
AWG 0 363A
AWG 00 432A
70mm2 443A
AWG 000 514A
90mm2 535A
Do these sizes sound right for what I wrote above?
Thanks for any comments
John
I would like to protect against a fire from the battery main cables. But I don't want to create a situation where the fuse occasionally blows for other reasons as this could for example then blow my alternator diodes, so I want to be absolutely certain that the fuse will not blow under any general usage circumstances but would protect against the situation where the wire became so hot that there was a danger of it catching on fire.
I think the biggest slow blow fuse is 750a and I would have imagined that this would always blow before a large cale (50-90mm) caused a fire ???
There has been some other pbo posts where the recommended fuse for the wire size has been suggested. Here they are...
cable size fuse
35mm2 264A
AWG 1 305A
50mm2 345A
AWG 0 363A
AWG 00 432A
70mm2 443A
AWG 000 514A
90mm2 535A
Do these sizes sound right for what I wrote above?
Thanks for any comments
John