Danfoss compressor and digital thermostat

Billyo

Well-Known Member
Joined
6 Nov 2016
Messages
219
Location
Swanage
Visit site
Hi all

I'm going to upgrade the mechanical thermostat on my fridge and freezer with an inkbird itc 1000f digital.

Currently the thermostat brown wire is connected to the C port on the compressor cuircuitboard and the blue to the port numbered 32

On the inkbird there are two port for cooling numbered 7 and 8.
If I keep the same wire does anyone know how the brown and blue connect on the inkbird?

Many thanks in advance!
 
Last edited:
Assuming this is simply a switch it likely won't matter. Any wiring diagrams for the compressor and / or switch ?

For any thermostat having a small deadband i.e. small difference between cut in and cut out temperatures is essential, otherwise you can reach a specific point when it will rapidly switch from on to off cycling and compressor motors definitely do not like this. So for a fridge Stat - On at say 4oC and off at 2oC.
 
Thanks, I can't seem to post photos from my phone and I don't have a computer at the moment as it lost an argument with a cup of tea. Will connect them up to the thermostat and just see what works......
 