"Built In Blocking Diode" wired correctly?

CaptainBob

Active member
Joined
7 Nov 2007
Messages
1,475
Location
North Yorkshire
www.yacht-forum.co.uk
I've bought a cheap 80W solar panel off eBay which has a "built in blocking diode" but looking at the wiring I'm not convinced it's "built in" correctly. Here's a picture of it with the MC4 wires coming out of the bottom of the junction box, and inside the box are two diodes, but they're wired across the wire connections, not in-line with them as I was expecting.

Do I need to install an additional diode in series in the positive output?

Here's the picture...

blockingdiode.jpg
 

CaptainBob

Active member
Joined
7 Nov 2007
Messages
1,475
Location
North Yorkshire
www.yacht-forum.co.uk
The wires pictured leaving that junction box, downwards in the picture, are the - and + (respectively) supply lines. They terminate with MC4 male and female connectors. I was simply intending to connect those directly into the solar input of my Marlec HRDi regulator.
 

CaptainBob

Active member
Joined
7 Nov 2007
Messages
1,475
Location
North Yorkshire
www.yacht-forum.co.uk
Thanks for your answers and time.

Unfortunately I'm not going to be able to find that out with damaging the panel irreparably.

What do you think about simply putting a Shottky Diode in series with the + out, just to be safe?
 

noelex

Well-known member
Joined
2 Jul 2005
Messages
4,805
Visit site
They are bypass diodes not blocking diodes and they are wired correctly. If you are using a solar regulator you do not need any extra diodes. Without a regulator I would add a blocking diode.
 

exfinnsailor

New member
Joined
18 Jul 2007
Messages
1,779
Visit site
Looks like two separate solar panels. The ground is on the left and the V+ for the first one is in the centre so you will get a voltage across these connections. The centre terminal is also the ground of the second panel and the terminal on the right is its output.

So its like two batteries connected together in series to give you a higher voltage. So the diodes are correct ....


..
 

Barry Jones

New member
Joined
5 Jun 2011
Messages
347
Location
East Anglia
myworld.ebay.co.uk
Yes it makes sense if these are bypass diodes for a dual panel system.
They are not blocking diodes as said by noelex.

Are all the three external connections disappearing into your single panel ?

Can the panel be wired without this junction box, as you won't need it for a single panel ??
 

CaptainBob

Active member
Joined
7 Nov 2007
Messages
1,475
Location
North Yorkshire
www.yacht-forum.co.uk
They are bypass diodes not blocking diodes and they are wired correctly. If you are using a solar regulator you do not need any extra diodes. Without a regulator I would add a blocking diode.

I'm using Marlec's HRDi charge regulator which states:

"Note: Solar panels must be fitted with appropriate blocking diodes, parallel panels having one each."

So presume if these are bypass diodes then I'll need to add a blocking diode. If so, would these be suitable (I plan to add more panels later)?

http://search.ebay.co.uk/280554041951
 

noelex

Well-known member
Joined
2 Jul 2005
Messages
4,805
Visit site
Yes those diodes look ok. If the handbook for the regulator advises fitting a blocking diode I would do so. (dont disonect the bypass diodes. Blocking and bypass diodes have different functions)

Its unusual most charge regulators disconect the panels when the light levels fall, but obviously not all.
 