I have a Fireblitz CO7B Car4bon monoxide Alarm.

I have a bank of 3 lead acid batteries under the bunk in my rear cabin in a vented compartment. I find that when the batteries are charged the alarm sounds when the batteries are in the absorption phase. This has happened many times in different locations when there has not been an obvious source of carbon monoxide. I thought that batteries produced hydrogen and oxygen so am a little surprised at the alarm sounding.

Has anyone else experienced the same?
 

VicS

Well-known member
Joined
13 Jul 2002
Messages
48,359
Visit site
I have a Fireblitz CO7B Car4bon monoxide Alarm.

I have a bank of 3 lead acid batteries under the bunk in my rear cabin in a vented compartment. I find that when the batteries are charged the alarm sounds when the batteries are in the absorption phase. This has happened many times in different locations when there has not been an obvious source of carbon monoxide. I thought that batteries produced hydrogen and oxygen so am a little surprised at the alarm sounding.

Has anyone else experienced the same?


As said already CO detectors are also sensitive to other gases, hydrogen being the one most likely to cause problems to a small boat owner.

I guess you need to seal your battery compartment more thoroughly and maybe also improve the venting. Hydrogen escapes very easily so very thorough sealing may be necessary and/or vent the batteries directly.
 
Last edited:

PaulRainbow

Well-known member
Joined
16 May 2016
Messages
16,289
Location
Suffolk
Visit site
I would expect that it would need excess gassing to set a Co alarm off, unless it was an unusually sensitive alarm. What type of batteries do you have, what make/model of charger and what voltages does the charger output ?
 

Irish Rover

Well-known member
Joined
5 Feb 2017
Messages
5,592
Location
Türkiye
Visit site
This happened to me last summer when my batteries were goosed and over charging - the rotten eggs stink was, however, obvious before the CO alarm activated.
 

DuncanHall

Member
Joined
14 Feb 2013
Messages
151
Location
Cardiff Yacht Club
Visit site
I would expect that it would need excess gassing to set a Co alarm off, unless it was an unusually sensitive alarm. What type of batteries do you have, what make/model of charger and what voltages does the charger output ?

I have 3 Trojan 31XHS batteries charged by a victron Multiplus with temperature compensation fitted. They are 2 years old. I do have to top them up a little but they seem to have plenty of capacity. Bulk is set to 14.82 but temperature compensation lifts that about 14.9.

The voltage is in line with Trojans recommendation.
see
https://cdn.taynabatteries.eu/datasheets/31XHS-Trojan-Data-Sheets.pdf
 

Lon nan Gruagach

Active member
Joined
12 Mar 2015
Messages
7,172
Location
Isle of Eigg
Visit site
Line the battery compartment with a catalyst to convert H + 2O back to water.
Ahh, mebby not, not given the price of platinum...
"recycle" bits of an old fuel cell and place a catalyst mesh in the compartment vent
If you can get hold of knackered batteries that have a catalyst built into the vent you could use that too.
 

PaulRainbow

Well-known member
Joined
16 May 2016
Messages
16,289
Location
Suffolk
Visit site
I have 3 Trojan 31XHS batteries charged by a victron Multiplus with temperature compensation fitted. They are 2 years old. I do have to top them up a little but they seem to have plenty of capacity. Bulk is set to 14.82 but temperature compensation lifts that about 14.9.

The voltage is in line with Trojans recommendation.
see
https://cdn.taynabatteries.eu/datasheets/31XHS-Trojan-Data-Sheets.pdf

Still wouldn't expect to set the alarm off every time the batteries are charged. I'd make double sure the batteries are not overly gassing.If not, perhaps moving the Co alarm would stop it going off.
 

yotter

Active member
Joined
3 Aug 2007
Messages
635
Location
Me Inverkip, boat Kip in winter, Craobh in summer
Visit site
My CO alarm went off while I was running an equalisation charge. Sterling 30A untra charger, flooded open lead/acid. I have never run the equalisation before, apparently is a good idea every so often. I slacked off the caps and 16V certainly produced some gassing. Good to know the alarm works, for H2 anyway.
Angus
 

lpdsn

New member
Joined
3 Apr 2009
Messages
5,467
Visit site
Has anyone else experienced the same?

I've experienced the same. Only very infrequently with the CO alarm, but is is quite common with the gas alarm.

Surprising I've found it happens even through the batteries aren't using excessive amounts of water.

I find leaving hatches open helps and closing the cabin door between cabin with the batteries and the galley with the gas alarm.
 

maxi77

Active member
Joined
11 Nov 2007
Messages
6,084
Location
Kingdom of Fife
Visit site
In submarines we had catalytic hydrogen burners to get rid of evolved hydrogen. I seem to remember they also got rid of CO so perhaps it could be a solution.
 

Plum

Well-known member
Joined
6 Jun 2001
Messages
4,385
Location
UK East Coast
Visit site
I have a Fireblitz CO7B Car4bon monoxide Alarm.

I have a bank of 3 lead acid batteries under the bunk in my rear cabin in a vented compartment. I find that when the batteries are charged the alarm sounds when the batteries are in the absorption phase. This has happened many times in different locations when there has not been an obvious source of carbon monoxide. I thought that batteries produced hydrogen and oxygen so am a little surprised at the alarm sounding.

Has anyone else experienced the same?

Yes, happens to me too. Was fairly frequent over a 2 year period but for the last two years much less frequent. The only thing I changed after the first 2 years was I changed the 18 year old battery charger to a modern CETK M200 battery charger.

www.solocoastalsailing.co.uk
 

DuncanHall

Member
Joined
14 Feb 2013
Messages
151
Location
Cardiff Yacht Club
Visit site
Still wouldn't expect to set the alarm off every time the batteries are charged. I'd make double sure the batteries are not overly gassing.If not, perhaps moving the Co alarm would stop it going off.

It does not happen every time but frequently following recharging overnight after heavy discharge.

Thanks all for the replies, I shall have to look at improving venting when on charge.
 

Minchsailor

Well-known member
Joined
2 Dec 2014
Messages
1,276
Location
N of Ardnamurchan, winter South of Oban
Visit site
I spent many years working on various forms of gas analysis and detection.

The detectors in mass produced alarms are relatively crude compared to their (and much more expensive) industrial equivalents.

A typical detector will have an alarm level of around about, say 100ppm. An H2 concentration of 250ppm is equivalent to 100ppm CO.

No surprise that is alarming.
 